Master electrician advise needed

Discussion in 'Home Improvement' started by Greybeard, Jul 9, 2019.

  1. Jul 10, 2019 at 5:47 PM
    #31
    War Machine

    War Machine SSEM # 5 3MW

    Joined:
    Aug 7, 2017
    Member:
    #8939
    Messages:
    16,933
    Gender:
    Male
    First Name:
    Jason
    Texas
    Almost every single residential underground and overhead drop in the country are run with aluminum wire. I’d bet every single member of this forum has aluminum wire incoming from the utility to their meter. I doubt any have had issues because of it.
    Aluminum wire, installed properly and to NEC regulations is in no way a fire hazard.
     
    TX-TRD1stGEN and bmf4069 like this.
  2. Jul 10, 2019 at 5:53 PM
    #32
    markg

    markg New Member

    Joined:
    Mar 17, 2019
    Member:
    #27711
    Messages:
    472
    Gender:
    Male
    First Name:
    Mark
    NC
    Vehicle:
    2007 TRD
    Smallest Aluminum available is #8 AFAIK.
    WM, you are correct, aluminum is ok when installed correctly, for feeders, branch curcuits, no.
    Todays aluminum is more of a composite (alloy) these days not 100% aluminum so expansion and contraction is limited.
    War Machine, which supply house you work for? Ever heard of Fox Rowden McBraier?
     
  3. Jul 10, 2019 at 6:45 PM
    #33
    Lambeau

    Lambeau New Member

    Joined:
    Oct 1, 2018
    Member:
    #20052
    Messages:
    130
    Gender:
    Male
    Vehicle:
    2019 Black Tundra Platinum 4x4
    XP Package, 20” Rockstar, 295/60/R20 Nitto G2, Line-X Bedliner, Undercover Elite LX Tonneau Cover, Remote Start, NSV Hood Bulge Light Bar, Predator Running Boards, TacoTunes SQ1 Sound System, Toytec Boss front coilovers, Toytec Boss rear shocks, Coachbuilder +2 rear shackles
    The discussion is not about service conductors. Hell my house has aluminum service conductors...they have crimp connectors and used Anti-oxidation compound. The discussion is about a small feeder circuit. No way I would run aluminum for that. Period.

    The projects I sign are only allowed to substitute aluminum for copper on the service conductors as long as they use crimp connectors and Noalox. I won’t accept the liability for any other copper wiring substitutions. Not worth the risk for small savings in my opinion.
     
    Last edited: Jul 10, 2019
  4. Jul 10, 2019 at 7:08 PM
    #34
    War Machine

    War Machine SSEM # 5 3MW

    Joined:
    Aug 7, 2017
    Member:
    #8939
    Messages:
    16,933
    Gender:
    Male
    First Name:
    Jason
    Texas
    There’s crimp connectors in your loadcenter?

    The application doesn’t matter. You said it’s a fire hazard. It’s not.
     
  5. Jul 10, 2019 at 7:11 PM
    #35
    BTBAKER

    BTBAKER DIFFERENT NAME. SAME JUNK.

    Joined:
    Nov 26, 2017
    Member:
    #11185
    Messages:
    5,426
    Gender:
    Male
    First Name:
    Brad
    Castle Rock
    Vehicle:
    2023 Ram Rebel
    True, I work with it daily. Although I have never seen underground primary or secondary conductor.

    But, I will say Copper is by far superior in just about every way other than costs and weight. Which is why utilities pull aluminum.
     
  6. Jul 10, 2019 at 7:18 PM
    #36
    BTBAKER

    BTBAKER DIFFERENT NAME. SAME JUNK.

    Joined:
    Nov 26, 2017
    Member:
    #11185
    Messages:
    5,426
    Gender:
    Male
    First Name:
    Brad
    Castle Rock
    Vehicle:
    2023 Ram Rebel
    I HATE Noalox. I have yet to see a contractor use it properly in substation applications. I also agree 100 percent with your response.
     
    Lambeau[QUOTED] likes this.
  7. Jul 10, 2019 at 7:23 PM
    #37
    BTBAKER

    BTBAKER DIFFERENT NAME. SAME JUNK.

    Joined:
    Nov 26, 2017
    Member:
    #11185
    Messages:
    5,426
    Gender:
    Male
    First Name:
    Brad
    Castle Rock
    Vehicle:
    2023 Ram Rebel
    I’m not sure of this. I don’t know everyone’s local rules but I can say my parents in the late 80s had to re wire their entire home to copper to meet code. I know all new home construction in CO is run with copper.
     
    Lambeau likes this.
  8. Jul 10, 2019 at 7:25 PM
    #38
    BTBAKER

    BTBAKER DIFFERENT NAME. SAME JUNK.

    Joined:
    Nov 26, 2017
    Member:
    #11185
    Messages:
    5,426
    Gender:
    Male
    First Name:
    Brad
    Castle Rock
    Vehicle:
    2023 Ram Rebel
  9. Jul 10, 2019 at 7:26 PM
    #39
    Lambeau

    Lambeau New Member

    Joined:
    Oct 1, 2018
    Member:
    #20052
    Messages:
    130
    Gender:
    Male
    Vehicle:
    2019 Black Tundra Platinum 4x4
    XP Package, 20” Rockstar, 295/60/R20 Nitto G2, Line-X Bedliner, Undercover Elite LX Tonneau Cover, Remote Start, NSV Hood Bulge Light Bar, Predator Running Boards, TacoTunes SQ1 Sound System, Toytec Boss front coilovers, Toytec Boss rear shocks, Coachbuilder +2 rear shackles
    This is a quote from International Association of Certified Home Inspectors:

    “Aluminum will become defective faster than copper due to certain qualities inherent in the metal. Neglected connections in outlets, switches and light fixtures containing aluminum wiring become increasingly dangerous over time. Poor connections cause wiring to overheat, creating a potential fire hazard. In addition, the presence of single-strand aluminum wiring may void a home’s insurance policies. Inspectors may instruct their clients to talk with their insurance agents about whether the presence of aluminum wiring in their home is a hazard, a defect, and a problem that requires changes to their policy language.”
     
  10. Jul 10, 2019 at 7:26 PM
    #40
    War Machine

    War Machine SSEM # 5 3MW

    Joined:
    Aug 7, 2017
    Member:
    #8939
    Messages:
    16,933
    Gender:
    Male
    First Name:
    Jason
    Texas
    Wire INSIDE the homes today are copper. Pretty much everything outside is aluminum, which is what OP is asking about.
     
    BTBAKER[QUOTED] likes this.
  11. Jul 10, 2019 at 7:27 PM
    #41
    Lambeau

    Lambeau New Member

    Joined:
    Oct 1, 2018
    Member:
    #20052
    Messages:
    130
    Gender:
    Male
    Vehicle:
    2019 Black Tundra Platinum 4x4
    XP Package, 20” Rockstar, 295/60/R20 Nitto G2, Line-X Bedliner, Undercover Elite LX Tonneau Cover, Remote Start, NSV Hood Bulge Light Bar, Predator Running Boards, TacoTunes SQ1 Sound System, Toytec Boss front coilovers, Toytec Boss rear shocks, Coachbuilder +2 rear shackles
    The wiring enters his house on both ends. The terminations are the most concerning.
     
  12. Jul 10, 2019 at 7:28 PM
    #42
    BTBAKER

    BTBAKER DIFFERENT NAME. SAME JUNK.

    Joined:
    Nov 26, 2017
    Member:
    #11185
    Messages:
    5,426
    Gender:
    Male
    First Name:
    Brad
    Castle Rock
    Vehicle:
    2023 Ram Rebel
    Not arguing. I just believe copper to be the superior option and worthy of the extra cost.
     
  13. Jul 10, 2019 at 7:32 PM
    #43
    War Machine

    War Machine SSEM # 5 3MW

    Joined:
    Aug 7, 2017
    Member:
    #8939
    Messages:
    16,933
    Gender:
    Male
    First Name:
    Jason
    Texas
    And the wire he’s asking about is not going to “outlets, switches and light fixtures”. It’s going from his loadcenter to whatever means he’s using to connect to the shed.

    The poor connections in those devices are prone to getting loose because they are moving and being manipulated. Copper is less likely to be an issue in that situation, not to mention that residential wiring devices are almost exclusively made for copper only.

    Aluminum wire installed per the NEC is not a fire hazard. It’s literally why the NEC exists.
     
    BTBAKER likes this.
  14. Jul 10, 2019 at 7:34 PM
    #44
    War Machine

    War Machine SSEM # 5 3MW

    Joined:
    Aug 7, 2017
    Member:
    #8939
    Messages:
    16,933
    Gender:
    Male
    First Name:
    Jason
    Texas
    In most cases, aluminum is brought in to the main lugs or breaker on the loadcenter. Copper is then used on the branches entering the home. I don’t see where the aluminum is entering his house at all.
     
  15. Jul 10, 2019 at 7:35 PM
    #45
    War Machine

    War Machine SSEM # 5 3MW

    Joined:
    Aug 7, 2017
    Member:
    #8939
    Messages:
    16,933
    Gender:
    Male
    First Name:
    Jason
    Texas
    I only debated the point that it’s a fire hazard. That’s 100% false if installed correctly.
     
  16. Jul 10, 2019 at 7:36 PM
    #46
    Lambeau

    Lambeau New Member

    Joined:
    Oct 1, 2018
    Member:
    #20052
    Messages:
    130
    Gender:
    Male
    Vehicle:
    2019 Black Tundra Platinum 4x4
    XP Package, 20” Rockstar, 295/60/R20 Nitto G2, Line-X Bedliner, Undercover Elite LX Tonneau Cover, Remote Start, NSV Hood Bulge Light Bar, Predator Running Boards, TacoTunes SQ1 Sound System, Toytec Boss front coilovers, Toytec Boss rear shocks, Coachbuilder +2 rear shackles
    Well nobody said it wasn’t allowed by code. Remember the code defines the minimum requirements. A good installation can exceed those requirements. I’ve inspected plenty of “problem” buildings that met minimum code requirements. Doing the absolute minimum is sometimes just cheap and irresponsible.
     
    BTBAKER likes this.
  17. Jul 10, 2019 at 7:38 PM
    #47
    Lambeau

    Lambeau New Member

    Joined:
    Oct 1, 2018
    Member:
    #20052
    Messages:
    130
    Gender:
    Male
    Vehicle:
    2019 Black Tundra Platinum 4x4
    XP Package, 20” Rockstar, 295/60/R20 Nitto G2, Line-X Bedliner, Undercover Elite LX Tonneau Cover, Remote Start, NSV Hood Bulge Light Bar, Predator Running Boards, TacoTunes SQ1 Sound System, Toytec Boss front coilovers, Toytec Boss rear shocks, Coachbuilder +2 rear shackles
    It’s a fire hazard when installed by a DIY homeowner not thoroughly familiar with installation practices. You’re twisting words.
     
    BTBAKER likes this.
  18. Jul 10, 2019 at 7:38 PM
    #48
    War Machine

    War Machine SSEM # 5 3MW

    Joined:
    Aug 7, 2017
    Member:
    #8939
    Messages:
    16,933
    Gender:
    Male
    First Name:
    Jason
    Texas
    Ok
     
  19. Jul 10, 2019 at 7:40 PM
    #49
    markg

    markg New Member

    Joined:
    Mar 17, 2019
    Member:
    #27711
    Messages:
    472
    Gender:
    Male
    First Name:
    Mark
    NC
    Vehicle:
    2007 TRD
    Any wiring/wire can be a hazard if not installed properly, by a professional or inexperienced person.
     
    Trooper2 and War Machine like this.
  20. Jul 10, 2019 at 7:42 PM
    #50
    War Machine

    War Machine SSEM # 5 3MW

    Joined:
    Aug 7, 2017
    Member:
    #8939
    Messages:
    16,933
    Gender:
    Male
    First Name:
    Jason
    Texas
    No, I’m not twisting anything. My advice would be to always hire an electrician. Pretty sure if he’s capable of running copper, he can run aluminum.

    Almost everyone has aluminum wire in their loadcenter. Most brands have aluminum bussing inside. There aren’t special connectors or terminations on those lugs. Those lugs have no idea what type of wire is attached to them. It’s not a fire hazard, period.
     
  21. Jul 10, 2019 at 7:46 PM
    #51
    Lambeau

    Lambeau New Member

    Joined:
    Oct 1, 2018
    Member:
    #20052
    Messages:
    130
    Gender:
    Male
    Vehicle:
    2019 Black Tundra Platinum 4x4
    XP Package, 20” Rockstar, 295/60/R20 Nitto G2, Line-X Bedliner, Undercover Elite LX Tonneau Cover, Remote Start, NSV Hood Bulge Light Bar, Predator Running Boards, TacoTunes SQ1 Sound System, Toytec Boss front coilovers, Toytec Boss rear shocks, Coachbuilder +2 rear shackles
    Dude you have some great posts on this site and I follow a lot of them. You’re giving horrible advice on aluminum wiring in this thread. I’m done arguing with you about it.
     
    BTBAKER likes this.
  22. Jul 10, 2019 at 7:47 PM
    #52
    markg

    markg New Member

    Joined:
    Mar 17, 2019
    Member:
    #27711
    Messages:
    472
    Gender:
    Male
    First Name:
    Mark
    NC
    Vehicle:
    2007 TRD
    Cooper is my preferred conductor. But, nothing wrong with Aluminum (now an alloy) if installed correctly, anywhere. (except branch circuit wiring)
    Utilities use it exclusively underground, overhead, high voltage to meters, to utility transformers and more.
    Aluminum in building feeders is no problem if done correct. They will require maint. (all mechanical connections should be tightened about every 2-3 years).
    Infrared testing should be done to determine what needs maint.
     
    BTBAKER and War Machine like this.
  23. Jul 10, 2019 at 7:55 PM
    #53
    bmf4069

    bmf4069 Yup, that's car parts in a dishwasher

    Joined:
    Sep 1, 2018
    Member:
    #18880
    Messages:
    7,343
    Gender:
    Male
    TX
    Vehicle:
    02 AC sr5 4wd v8
    Every time I use AL, I tighten it, then move the wire around. You can usually get another 1/2 - 3/4 turn on it. And always noalox.
     
    TX-TRD1stGEN likes this.
  24. Jul 10, 2019 at 8:02 PM
    #54
    BTBAKER

    BTBAKER DIFFERENT NAME. SAME JUNK.

    Joined:
    Nov 26, 2017
    Member:
    #11185
    Messages:
    5,426
    Gender:
    Male
    First Name:
    Brad
    Castle Rock
    Vehicle:
    2023 Ram Rebel
    Utilities DO NOT exclusively use aluminum. I’ve working for a utility (5 largest in the US) for 20 years so I’ll argue this all day.
    No way utilities take outages 2-3 years to check connections and I’m guessing most buildings etc don’t either I can assure you of this even though I agree it’s a good practice in theory. That’s what proper hardware and torque specs are for. And yes, I use 30,000 dollar FLIR equipment on the regular and it’s great for finding hot spots but I would bet most of this technology isn’t utilized by the average Joe or most commercial buildings unless problems arise.
     
    Last edited: Jul 10, 2019
    War Machine likes this.
  25. Jul 10, 2019 at 8:03 PM
    #55
    War Machine

    War Machine SSEM # 5 3MW

    Joined:
    Aug 7, 2017
    Member:
    #8939
    Messages:
    16,933
    Gender:
    Male
    First Name:
    Jason
    Texas
    At least we can agree on that.

    No hard feelings.

     
  26. Jul 10, 2019 at 8:08 PM
    #56
    BTBAKER

    BTBAKER DIFFERENT NAME. SAME JUNK.

    Joined:
    Nov 26, 2017
    Member:
    #11185
    Messages:
    5,426
    Gender:
    Male
    First Name:
    Brad
    Castle Rock
    Vehicle:
    2023 Ram Rebel
    :rofl::rofl:
     
    War Machine[QUOTED] likes this.
  27. Jul 10, 2019 at 8:15 PM
    #57
    Azblue

    Azblue Beer is Good Ban Moderator

    Joined:
    Nov 17, 2017
    Member:
    #11025
    Messages:
    6,321
    Gender:
    Male
    The Dirty T
    Y'all are being way to serious about this wire thing. All the OP needs is this:

    orange-southwire-general-purpose-cords-23098803-64_1000.jpg
     
  28. Jul 11, 2019 at 6:14 AM
    #58
    markg

    markg New Member

    Joined:
    Mar 17, 2019
    Member:
    #27711
    Messages:
    472
    Gender:
    Male
    First Name:
    Mark
    NC
    Vehicle:
    2007 TRD
    Tell me, show me where utilities use copper.
    You will not find a utility in NC/SC or other states I've done work, that uses copper.
    I have been in the electrical industry for over 35 years, got my NC unlimited electrical contractors license in 1982 and NEVER seen a utility use copper. (unless on premises and specified by engineer or project owner)
    Utilities use compression connection, not required to tighten.
    Unless your are doing sub-station and it is specified by/for the building owner/engineer, or other utility in premises specified copper, ALUM will be used by the utility company.
     
    War Machine likes this.
  29. Jul 11, 2019 at 6:35 AM
    #59
    War Machine

    War Machine SSEM # 5 3MW

    Joined:
    Aug 7, 2017
    Member:
    #8939
    Messages:
    16,933
    Gender:
    Male
    First Name:
    Jason
    Texas
    I see that electricians, utilities guys, distributors, and engineers arguing with each other isn’t just a Texas thing. I feel right at home! :rofl:
     
    bmf4069 and BTBAKER[QUOTED] like this.
  30. Jul 11, 2019 at 6:36 AM
    #60
    BTBAKER

    BTBAKER DIFFERENT NAME. SAME JUNK.

    Joined:
    Nov 26, 2017
    Member:
    #11185
    Messages:
    5,426
    Gender:
    Male
    First Name:
    Brad
    Castle Rock
    Vehicle:
    2023 Ram Rebel
    Sure, I’ll show you. I’m at my desk but when I go out I’ll walk into the yard. I’ll send you a picture if you need your proof. And even a compression fitting is bolted onto something so that makes zero sense as you say all “mechanical connections” should be checked for tightness every 2-3 years. I can send you a picture of my credentials/diploma to if you like?
    I would rather not argue about this. I’m not a commercial electrician. I’ll leave that to the experts but give the advice I’m comfortable with. I am, however a long time employee of the utility industry and I can tell you for fact a lot of underground 500/750/1000 MCM copper is pulled. In fact, even more so now in CO with all the grow facilities.
     